Hakubi_Washu writes "LiveJournal has posted their official analysis of what happened last Friday. Apparently someone "accidentally" pushed the emergency power off (which should keep all power off, even UPS), reset it and ran off. They had problems to come back up fast, because of "9 machines with faulty motherboards with embedded NICs that don't do auto-negotiation properly", Machines not fully rebooting for analysis reasons and few others. "
+ -
story
This discussion has been archived. No new comments can be posted.
The Fine Print: The following comments are owned by whoever posted them. We are not responsible for them in any way.
 Full
 Abbreviated
 Hidden
More
Loading... please wait.
  • by Anonymous Coward on Thursday January 20 2005, @03:28PM (#11423679)

    They should be using OpenBSD. It can run right through power failures [grub.net]
  • by geoffspear (692508) * on Thursday January 20 2005, @03:28PM (#11423686) Homepage
    Don't let your clients near the Big Red Button without an escort. Preferably an armed one.
  • faulty mobo's (Score:5, Interesting)

    by Lifthrasir (646067) on Thursday January 20 2005, @03:29PM (#11423697)
    so, they had faulty motherboards, knew about it, and didn't do anything to fix it before they had a major outage?
    • The solution is even funnier...
      To get them back up they need somebody at the NOC to plug them into a compatible switch, let them autonego, then switch them to their real switch.
      This is how a company with Millions of paying accounts runs its data center, and they even knew about the problem!
  • Now, if slashdot could fix their servers, so we wouldnt get thoose annoying 503 sites..
    I havent seen them that much lately, but then i havent been online that much either...
    • Now, if slashdot could fix their servers, so we wouldnt get thoose annoying 503 sites..

      You get 503 sites? I only reach one at slashdot.org

      Then again, you're a subscriber. Who knows what goodies you lucky few get here...
  • Oppsie (Score:5, Funny)

    by darkstar949 (697933) on Thursday January 20 2005, @03:29PM (#11423705)
    "I'll just set my coffee down here, and..."
    ...
    "Oppsie, I hope that button wasn't anything important."
  • by bsd4me (759597) on Thursday January 20 2005, @03:30PM (#11423706)

    Ah, the famous History Eraser Button rears its ugly head. I think that everyone who has worked in a large datacenter or lab environment with one of these has a story to tell...

    • by scribblej (195445) on Thursday January 20 2005, @04:06PM (#11424157)
      I'll go right ahead then. I was consulting for State Farm installing machines that were supposed to help with the Y2K problem. Hell if I know, I just got the box, went to the site, installed it and made sure it was working. Easy. I had five to do a week, and would be done by Tuesday morning and helping out other contractors on similar projects.

      I'll never forget my visit to the State Farm DSO in Detroit, MI. I'd just physically installed the new machine, at the bottom of a rack, and stood up.

      Stood up putting my shoulder right into the unprotected "History Eraser Button" on the wall. The screams of the employees working int he datacenter could be heard all the way back home in Chicago, I've no doubt.

      Then it turns out the fuses which will reset the systems in the datacenter are in a locked cabinet.

      Then it turns out no one on site has a key.

      Fortunately, I found that the cabinet will pop open if you kick it hard enough. Hey, I was panicking, okay?

      And get this. After it was all over and I realized I probably wouldn't get killed by anyone... they told me "It's okay, this happens all the time. The guy installing the A/C unit last week did it too."

      Maybe they should have put a cover over the damn button then. Morons.

        • If I ever catch anyone putting a cover over a critical piece of safety equipment, like an Emergency Power Cutoff switch, I'll put their head on a pole in front of the data centre as a warning to others.

          You of all people should realize that putting someone's head on a pole in front of a data centre is dangerous. For one, it tends to become a disease vector, as for some mysterious reason everyone feels the need to touch it. Rats are usually attracted to the smell, and you know how rats wreak havock on eth
  • /.s current poll [slashdot.org] now?
  • Fascinating read (Score:5, Insightful)

    by Saint Aardvark (159009) * on Thursday January 20 2005, @03:31PM (#11423728) Homepage Journal
    It's amazing how much you can learn from things going horribly wrong. :-)

    Congrats to the LJ folks for getting things working, taking the time to do it right, and giving an admin's-eye-view into what actually happened.

    • Agreed. I always appreciate when people explain how large scale outages happened, were able to happen, how they fix it, and what they do to prevent it happening again. It's useful (and good for your employment status) to learn from other people mistakes rather than your own.
      So Slashdot - what are all the 500 errors about then? :)
  • by Rosco P. Coltrane (209368) on Thursday January 20 2005, @03:33PM (#11423755)
    Apparently someone "accidentally" pushed the emergency power off

    They had to power back on when they realized deadjournal.com [deadjournal.com] was already taken...
  • by TrevorB (57780) on Thursday January 20 2005, @03:33PM (#11423759) Homepage
    If Mr. "I Pushed The Big Red Button"'s personal information ever gets published....

    LJ's active user base is easily 10x that of Slashdot's. We'd have to come up with a new term for the internet event that pales any slashdotting that ever came before.
  • Auto-negotiation (Score:4, Informative)

    by stilwebm (129567) on Thursday January 20 2005, @03:34PM (#11423772)
    When I first moved company servers in to a new colo four years ago, their engineers advised me that I should turn auto-negotiation off on every port, including our switches and host NICs. I asked why they recommended this and they replied, "trust us, auto-negotiation causes problems when you least expect it." I went ahead and fixed the port speeds everywhere. Now I understand why.
    • by jjgm (663044) on Thursday January 20 2005, @03:56PM (#11424030)

      Sounds like a classic Cisco problem. I don't know what switches LJ were plugged into, but for years most Cisco switches would autonegotiate 100/half-duplex if the NIC was locked to 100/full; conversely, sometimes, NICs would autonegotiate 100/half if the Cisco was locked to 100/full.

      They're cheeky enough to document this [cisco.com] now. It's a feature, not a bug! Honest!

      • by Anonymous Coward on Thursday January 20 2005, @04:11PM (#11424235)
        Go ahead and read up on how auto-negotiation works. I'll wait...

        No, really. Go read up on it...

        Okay, since you don't bother reading up on it, and since you claim that someone's cheeky because they *document* what happens when you misconfigure a connection, I must conclude that you, sir, are indeed an idiot.

        (To summarize for those of you who won't bother to look it up, a NIC can sense the carrier for 100, so it can differentiate 10/100. Full and half are actively negotiated by the two sides of the connection. If side 'A' is hard set to 100/full, it won't negotiate with the other side. Hearing no negotiation, side 'B' will assume the NIC doesn't support full duplex connections and failover to half duplex. This is the proper, standardized, documented behavior. Anything else would require the psychic interface spec that *still* hasn't been finalized.)
  • by stratjakt (596332) on Thursday January 20 2005, @03:35PM (#11423784) Journal
    What do you mean, ran off?

    Ran off skipping and giggling, like a 13 year old who just put toothpaste on the toilet seat?

    Or do you really mean, slunk off, like my dog does when I walk in and find her curled up on top of the remains of the remotes for the TV, TiVo, DVD player and stereo?

    My dog likes remote controls more than snausages.

    OT: Anyone know where (brick and mortar) to get a replacement (original) TiVo remote?
    • Ran off skipping and giggling, like a 13 year old who just put toothpaste on the toilet seat?

      By any chance, was his name "Zero Cool"?
  • Credit (Score:5, Informative)

    by XorNand (517466) on Thursday January 20 2005, @03:38PM (#11423819)
    Anyone who's a paid member of LJ can get a 2-week credit here [livejournal.com].
  • I must compliment LJ for at least being honest with their system... many would lie and say "it was the datacenter's fault".

    They at least admit their own systems weren't perfect... and clearly explained each fault they observed.

    Good info.
  • by ShatteredDream (636520) on Thursday January 20 2005, @03:41PM (#11423853) Homepage
    *crickets chirping* That's the sound millions of teenage girls not using up bandwidth and disk space talking about boys, jcrew and high school/college drama.
  • machine failure (Score:4, Insightful)

    by br00tus (528477) on Thursday January 20 2005, @03:41PM (#11423858)
    "They had problems to come back up fast, because of '9 machines with faulty motherboards with embedded NICs that don't do auto-negotiation properly", Machines not fully rebooting for analysis reasons and few others.'"

    I was a sysadmin at a Fortune 100 company with thousands of servers. Every Saturday evening, we rebooted all of our servers. We almost always had several machines which would not come back up for one reason or another - so we dealt with it then, on Sunday morning, instead of during the week when a reboot of a critical machine that did not work would be much worse. Scheduled reboots are a part of good systems administration. If once a week is too often, then once every two weeks, or once a month. With this much failure, I'm almost certain they never did scheduled reboots. They had two failures - their power failed, and then their lack of planning allowed for so much to go wrong a result of that.

    • Re:machine failure (Score:5, Insightful)

      by rjstanford (69735) on Thursday January 20 2005, @03:47PM (#11423933) Homepage Journal
      One of the last steps of our standard deployment was a full hard shutdown and restore from backup. This was shceduled to happen approximately a week before bringing the machines live - after a lot of data setup had been done.

      Many customers - and internal staff - really, really got scared at that point. The thing is, if you don't trust your backups, what good are they? Its amazing what things got taken care of and found during double-checks the week before the backup/restoration test.

      Oh, and we always went with scheduled reboots as well, for very much the same reason as you mentioned. An hour a month of scheduled downtime is almost always available - usually we booted every week and had an optional downtime window on a monthly basis. And if your (talking to readers here, not parent) organization can't afford to be without a single machine for a 2-3 hour block once a month, WTF is your plan to handle a hardware failure? Prayer?
    • Every Saturday evening, we rebooted all of our servers

      Yeah, we had servers like that once, too. Ba-da-bing! Thanks, I'll be here all week.

      On a serious note, am I the only one here who thinks a world in which no one questions a policy like that is insane? We've had critical, and I mean critical, servers that have uptimes measured in years. But then again they run NetWare, or OS/400, or MVS, or.... ABW.

      Scheduled reboots are a part of good systems administration

      Yeah, scheduled, as part of a disaster re

      • You sir, sound like a man who needs a load balanced cluster. If you're relying on individual boxes staying up to meet your SLA's, your career is a ticking timebomb.
  • by GillBates0 (664202) on Thursday January 20 2005, @03:42PM (#11423873) Homepage Journal
    ...when I was on AOL and I hit the X and I couldn't talk to my AOL Buddies anymore.

    And I was like OMG I shut off the internets and stuff!!1!!

    And i called the AOL helpdesk and they helped turn it back on.

  • by phaetonic (621542) * on Thursday January 20 2005, @03:48PM (#11423942)
    I have run across this issue in data centers numerous times. This still occurs with the latest hardware, no matter what vendor or OS. I have this problem on SunFire280Rs and Compaq DL360s. What it comes down to is the switch being used in the data center and the settings in the OS. Typically, data centers set their switch to forced 100-full (unless of course they are using fibre or Gb). The OS must be set to force its NICs in the same mode, or they will either drop alot of packets. Sounds like a disconnect in communications between the NOC and the customer.
  • by Mordant (138460) on Thursday January 20 2005, @03:52PM (#11423981) Homepage
    They ought to have out-of-band (OOB )serial-console access to their servers via a terminal server for any number of reasons, including this one; if they'd implemented OOB console access, they could've sshed into the terminal server, gotten onto the consoles of the servers in question, and used ifconfig to fix the duplex issue.

    Why they don't seem to grasp this is beyond me . . . anyone running a public-facing, high-volume service should have OOB access to all servers, routers, switches, firewalls, etc. . . . it's just common sense.
  • The one [livejournal.com] they tell you about and the real [livejournal.com] one.
  • No! (Score:3, Insightful)

    by Saeed al-Sahaf (665390) on Thursday January 20 2005, @03:57PM (#11424031) Homepage
    embedded NICs...

    Who in their right mind goes with the on-board NIC in a server environment?

    • Re:No! (Score:3, Interesting)

      Who in their right mind goes with the on-board NIC in a server environment?

      Are you kidding?

      How about everyone? Regardless of PC, Sun, Alpha or whatever hardware.
  • Accidents happen (Score:3, Interesting)

    by Migraineman (632203) on Thursday January 20 2005, @04:07PM (#11424176)
    About a decade ago, we had a series of "incidents" with the EPO button in the software lab. Shortly after a serious lab upgrade (due to constantly blowing breakers,) someone decided to test the EPO switch (it was a bit of a novelty at the time.) *click* "Cool, it works. Hey, how do you reset this thing?" Turns out you needed to have a key to reset it. It took about 4 hours to find someone who had the key. That one got replaced with the Mark II resetable switch ...

    About a month later, one of the managers was giving a prospective new-hire a tour. He got to the software lab, and started blathering about "don't ever push the red switch" as he put his finger on the switch ... *click*

    So some einstein decided that the Big Red Switch was "dangerous" and put a plexi cover over it - the same kind that goes over the thermostat control, and the same kind that has a key lock. Yep, about six months later we had a gen-you-ine emergency. One of the HP 9000/300 monitors went crispy, and was snorting smoke and sparks. One of the software folks went to hit the Big Red Button, but was somewhat nonplussed to find a locking cover over it. She took the co-located fire bottle, sheared the cover off, pressed the button, then got to use said fire bottle on the monitor.

    So the cover gets replaced again, though this time with a non-locking cover. At some point, the software server stack needed to be relocated into the corner with the Big Red Button. Another einstein discovered that it was inconvenient to slink behind the equipment rack - the cover kept bashing him in the neck or shoulder. So he removed it, thinking that accidental presses wouldn't happen because the button was obstructed by the server stack. (yep, inaccessible = useless.) Some time later, the equipment was being jockeyed for an upgrade, and one of the big SCSI cables snagged the Big Red Button and *click* ...

    All these shenanigans happened in the space of one year, and I got tired of the thrash. I measured the space between the back of the switch and the faceplate - just over 3/4 inch. I cut a horseshoe shape out of 3/4 plywood, and hung it on the switch shaft. In and emergency, it's really easy (and obvious) to remove it. Gravity keeps it there otherwise. No problems since ...

    • They usually are in a server room. They're for emergencies. Ours have red cages around them and a BIG RED SIGN, you have to basically punch them.
    • Typically these types of devices are just inside the door to the rooms that they cut off. This way Fire & Emergency personnel can get to them quickly and easily.

      Generally the buttons themselves are behind plexiglass lids that easily flop up or behind breakable glass.
    • Technically, yes. I'm hoping that if LJ decides to implement such a scheme (let's call it "LEPO" for "Leisurely Emergency Power Off") that they run it past the fire marshal or the code inspectors first, who may have another opinion about how smart this idea is.

      "If it's stupid and it works, it's not stupid."
    • Isn't that circumventing the purpose of the EPO? If there's a smokey fire in there and the firefighters have to enter the room and start spraying water around, won't a few machines glowing for four minutes after the EPO was pressed put them in danger of electrocution? Or force them to wait four minutes beore they can enter?

      It's not so much that the firefighters spraying water are worried about getting electrocuted via current conducting through the water itself... it's more about worrying bout stumbling i
    • Re:Also, (Score:3, Informative)

      "Why do we even have that button?" Because it's basically required by law. Covering them with a plastic cover doesn't seem to help either--Internap did that the *last* time someone hit the EPO button in this datacenter.
    • I'm surprised that they didn't have their own little UPSes to bring the system down cleanly before. Sure, the facility is supposed to provide power at all times, even if there's a power grid interruption, but that doesn't get tested very often and isn't under your control. Furthermore, in the event that the facility's power is actually going to go out, there isn't any way for the machines to find this out and shut down cleanly.

      Unfortunately, this would defeat the purpose of the "Big Red Button", which

    • LiveJournal got hit the hardest, they had some IDE drives on their servers, doh!

      I was unaware that SCSI drives had the ability to run without power - thanks for the info!